Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Description of LED patterns on access readers, and how to change them

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Description of LED patterns on access readers, and how to change them
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa139513
    sesa139513
  • Carl_Slack
    Carl_Slack
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2084 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Description of LED patterns on access readers, and how to change them

Picard Product_Support
‎2018-09-06 02:52 PM

Issue

Description of LED patterns on access readers, and how to change them

Product Line

Andover Continuum

Environment

Continuum site

Cause

Description of LED patterns on access readers, and how to change them

Resolution

How to control LED patterns on access readers ****For all Continuum controllers that support access control and modules except AC1 and AC-1A****

NOTE: AC1 and AC1A only support the Alternate LED pattern. Card Reader LED Patterns The LED pattern of the card reader is determined by the creation of an InfinityNumeric called AccessLEDPattern. TAC LED Pattern (AccessLEDPattern=0) This pattern is transaction based, meaning the reader LED indicates the state of the access transaction.

Solid Red No door configured for this reader channel. The system will not process any transaction coming from this reader.
Solid Green Door configured on this reader channel. System is ready to process an access transaction.
Solid Red for 3 seconds following an access transaction Invalid attempt.
Rapid flashing following an access transaction Valid access
Slow flashing following an access transaction System is waiting for information needed to process the transaction. For example, transaction is being processed (remote validation) or the system is waiting for user entry. (PIN needed after card swipe.)

 

Alternate LED (Default) Pattern (AccessLEDPattern=1)
This pattern follows the state of the door lock itself. This is the default LED pattern. 

Solid Red Door is locked
Solid Green Door is unlocked
Rapid flashing following an access transaction Invalid attempt
Slow flashing following an access transaction System is waiting for information needed to process the transaction. For example, transaction is being processed (remote validation) or the system is waiting for user entry. (PIN needed after card swipe.)

 

The above LED patterns are the most commonly used. LED Patterns 3 and 4 are for CardKey and Dorado Model 780 ABA Reader/Keypad please refer to the documentation in the ACX II Controller Operation and Technical Reference Guide for more information on these readers and further information on LED Patterns

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2860
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore