Delete all remote I/O modules in an application
  • Delete all remote I/O modules in an application
  • Kim_Baze
    Kim_Baze
‎2018-09-06 12:56 PM
The option to add or decrease the number of remote I/O modules using the Remote IO Wizard is shown, but what is the process to eliminate all modules?
I/A Series WorkPlace Tech
Eliminate all I/O modules using the Remote IO Wizard
  1. Open the ADI/Remote IO Wizard from the Applications menu.
  2. With the Remote IO Wizard window displayed hit the Back button and select "none" and click Next.
  3. When prompted with "Do you wish to continue?" select yes and all the RIO Input and output tags will be removed from the drawing.
    Note: objects that were linked to these tags that are no longer being used must be "cut" from the drawing manually.
  • TAC IA Series
  • 6846