Delete/Replace an I/O Module in Menta Device Specification

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Delete/Replace an I/O Module in Menta Device Specification
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1328 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Delete/Replace an I/O Module in Menta Device Specification

Picard Product_Support
‎2018-09-06 01:57 PM

Issue

It is only possible to remove the last I/O module in the Options > Device Specification list.  And it cannot be removed until all references to hardware I/O are also removed.  Attempts to delete it prior to this will result in:

"The I/O Modules cannot be removed because it is bound to the following blocks:"

If it is the second I/O module of 8 that needs to be changed to a different type, this describes the most efficient way to remove I/O references and put them back.

Environment

Menta

Cause

This warning is a precaution against leaving stranded hardware I/O points if the modules they are associated with are deleted.

Resolution

  1. In Menta, go to Options > I/O Configuration Table
  2. Click the "Bound to" column header twice to sort by bindings with hardware I/O listed first
  3. In this example, remove I/O Module #8.
    1. Find all references to "M8-"
    2. Double click each output. Change the Bind to option to Not connected
    3. Double click each input. Change the Bind to option to Network Variable.  Leave the Network Address blank.
  4. Repeat these steps for the I.O module that will be replaced as well as any higher in the list.
  5. Go to Options > Device Specification
  6. Remove all I/O Modules down to the one needing to be replaced.  Add them back in in the desired configuration.
  7. Go back to Options > I/O Configuration Table
  8. Click the "Bound to" column header once to sort by bindings with Network Variables listed first
  9. Double click each converted input and output and switch them all back to Physical Input, Linear Analog Input, Non-linear Analog Input, or Physical Output, where appropriate.
  10. The physical I/O bindings are recalled when the point is changed back to physical I/O.
    Note:  The sensor configurations (0..10V, 2..10V, etc) will need to be set up again.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4929
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of