Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Dehumidification using Xenta 121-FC

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Dehumidification using Xenta 121-FC
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1631 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Dehumidification using Xenta 121-FC

Picard Product_Support
‎2018-09-06 01:27 PM

Issue

Dehumidification using Xenta 121-FC

Environment

  • Xenta 121-FC
  • Xenta 121-HP

Cause

Some aspects of how the dehumidification mode in the Xenta-121 operate are undocumented.

Resolution

The dehumidification feature of the Xenta 121 can operate either by turning on external dehumidification equipment using one of the digital outputs or, if no external equipment is provided, it will use the cooling for dehumidification. In the latter scenario, the heat continues to be operational when the cooling is forced for dehumidification. Additionally, if there is an outside air damper, it will be controlled to its minimum position before forcing the cooling on.

When is external dehumidification enabled?

  • For On/off cooling, cooling is enabled for dehumidification when the nvoDehumidActive value is greater than 10% and is disabled when the nvoDehumidActive value drops below 5%.
  • For all other types of cooling, nvoCoolPrimary is set to match the nvoDehumidActive whenever it is a greater than cooling PID output + 5% or whenever the cooling PID output is less than 5%.

The dehumidification feature can be configured using the ZBuilder configuration tool. However, the individual features can also be accessed via the points listed below using either Vista Workstation or another Lon management tool such as LonMaker:

Applic

UCPTappOptions

Bit Usage If FALSE If TRUE Additional notes
5 Dehumidification control enable Not active Active  
6 Dehumidification type Internal External Only applicable if bit 5 = true. External control can be hardwired or via SNVT. Internal will force cooling as a dehumidification method.
7 External dehumidification active on Open contact Closed contact Only applicable if bits 5 and 6 are both true.

UCPTappOptions2

Bit Usage If FALSE If TRUE Additional notes
7 External dehumidification type Digital Analog If true then the RH reading is mirrored to the analog output (0-100% = 0-10V). Only applicable if UCPTappOptions bits 5 and 6 are both true.
Labels (1)
Labels:
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 5885
  • dehumidify
  • humidity
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of