Defining Coefficients (Gain and Offset) in XBuilder Device Templates

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Defining Coefficients (Gain and Offset) in XBuilder Device Templates
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • SESA116857
    SESA116857

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1619 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Defining Coefficients (Gain and Offset) in XBuilder Device Templates

Picard Product_Support
‎2018-09-07 03:11 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-28 07:42 AM

Issue

Modbus (or other 3rd party communications protocol) not displaying correct value even though coefficients (gain and offset) have been defined

Product Line

TAC Vista

Environment

  • XBuilder
  • Device Template

Cause

The Xenta 913/731 uses an abnormal equation when applying the coefficient in device templates for 3rd party interfaces: y=m(x+b)

Traditionally, the slope-intercept form is used when applying a coefficient: y =mx+b

This means that the gain in the coefficient is applied after the offset rather than before it.

Resolution

If you have the information that fits a traditional slope-intercept form and need to apply a coefficient in a XBuilder device template then use the following as your variables where m and b are from the slope-intercept form equation:

Gain: m
Offset: b/m


The following is an example of one manufacturer's specifications for its Modbus values and how to correctly enter them into the device template:

For a temperature sensor reading that is being sent as a Modbus point a certain manufacturer specifies that to correct the raw value the following should be used:

  • Gain = 0.1
  • Offset = -40

Incorrect Offset 2.png

 

However, the manufacturer assumes the standard slope-intercept form will be used, so entering the data without any adjustments would cause the value to be converted incorrectly in the Xenta Server.

For example, if the temperature was 80 °F then the raw Modbus value would be 1200 and the Xenta Server would apply the coefficient as y=0.1(1200+(-40)), simplified as y=120-4. This means the Xenta Server would return a value of 116 °F instead of 80 °F.

 

In order to fix this the offset should be multiplied by the gain in order to compensate for the difference in how the Xenta Server utilizes the coefficient compared to how the 3rd party manufacturer intended it to be used. So the following would be used:

  • Gain = 0.1
  • Offset = (-40)*0.1 or -400

Correct Offset 2.png

 

Now, with a temperature of 80 °F the raw Modbus value will still be 1200 and the Xenta Server will apply the coefficient as y=0.1(1200+(-400)), simplified as y=120-40. The Xenta Server now returns the correct value of 80 °F.


 

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 3082
  • bacnet
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore