Decoding LANMON 3 errors

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Decoding LANMON 3 errors
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1811 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Decoding LANMON 3 errors

Picard Product_Support
‎2018-09-06 01:31 PM

Issue

After running LANMON 3 on an I/NET C-LAN, it may return some error codes. The list below will help determine what they mean and the best way to address them.

Environment

  • I/NET Controller LAN
  • LANMON output text file

Cause

Controller LAN errors captured by the LANMON program.

Resolution

One of the most useful new features of LANMon 3.0 is the detection and labeling of several types of communications errors. The label associated with the detection of a communications error is stored in the disk file just in front of the communications packet to which the error label applies. The error labels are presented in ASCII text along side the hexadecimal data. This text should allow most I/NET technicians to perform some level of useful investigation into controller LAN communications problems and reduce the necessity for sending LANMon files in to Technical Service for analysis. The following paragraphs lists the error descriptions associated with the type of errors detected by LANMon. The Bold text represents the label you will see on the screen or in the capture file when LANMon detects that type of error.

ERR: Retry

This error indicates that LANMon has detected a retransmission of the same command. This is the most common error type and can be used to find which controllers are having problems receiving from others. You should reference the destination and source addresses listed in the retry packet and accumulate/record this information. If there is a prevalence of specific nodes (destination or source) showing up in the retry packets, this would serve as a significant pointer to examine for network problems in that physical area (possibly in the cabling, environmental disturbances, power, grounding, and controller hardware and/or application software)

ERR: LAN reconfiguration

This error indicates that LANMon detected the occurrence of a LAN reconfiguration. This is a normal expectation when a controller/node is added or removed from the network as a result of LAN cable disconnect or power. When intentional changes are not in-work on the network configuration, a LAN reconfiguration is typically the result of several sequential errors (typically retry’s) which prompts the sending controller/node to initiate a LAN reconfiguration on the basis that it appears a node has been lost and everyone needs to have a new picture of the network layout.

ERR: SDLC CRC Error

This error indicates that the LANMon Tap received an RS485 packet with incorrect CRC indicating the packet is corrupted in some way. This error results from data distortion on the cabling or from intermittent disruptions such as from EMI, noise or grounding fault. With this error, the primary address you are interested in is the source address. If you are seeing a number of CRC errors from the same node address, or a collection of node addresses, you may want to look for cabling or loading problems in that area, or the length of cable getting to the area. You should make note of where LANMon is positioned when seeing this error. The error could be expected to get worse as to get further away from the reporting node address. For this reason, it is often recommended that you perform LANMon captures and analysis from at least two points on the network and those points should be the two most distant ends of the network.

ERR: LAN master conflict with ##

This error indicates LANMon has detected a NULL command output from a controller/node other than the currently recorded LAN master. The ## number will show the address of the node currently understood to be the LAN master. The packet following this error message will contain the address of the contending LAN master. This master conflict error is frequently the result of multiple simultaneous LAN reconfigurations. There should only be one LAN master and it is the function of that one LAN master to output the NULL command each time the token makes one pass around to all the network addresses and arrives back at the LAN master.

 

The following error descriptions will be encountered far less frequently and are not typically used for LAN diagnosis.

ERR: Bad address

LANMon detected a destination or source address greater than 3F16 (6310)

ERR: Bad NULL

LANMon detected that NULL was sent out without the same destination and source address, or without the broadcast header.

ERR: Bad reconfigure

LANMon detected that reconfigure command “01” was sent out without the same destination and source address, or without the FF broadcast header.

ERR: Bad token

LANMon observed what appeared to be a token command but had byte count greater than 3, or had destination and source addresses the same.

ERR: Frame overrun

LANMon received >160 bytes on the Async port from the LANMon Tap which exceeds design limits/expectations.

ERR: Frame underrun

Async frame from LANMon Tap to PC was considered too short to contain any SDLC (CLAN) data.

ERR: Lost frame synch

The LANMon program running in the PC got out of synch with the data stream from the LANMon Tap. This should be an unusual error. If it is repeatedly encountered, You can try running the LANMon utility on a faster PC, or you can try running it with Monitor mode OFF. B E1 m N O

ERR: Bad frame CRC

The LANMon program detected a CRC error in the Async frame of data from the LANMon Tap. With the standard short (6 ft.) RS232 cable between the PC and Tap, this should be a very infrequent error.

ERR: Unknown error code

This is a catch-all error indication intended to present any error codes returned from the SDLC controller in the Tap that are not currently defined. You should not see this error message.

ERR: Frame too short

The Async frame of data from the Tap to the PC is considered too short to contain a valid SDLC packet.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5752
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore