Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Daylight saving settings when using external time controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Daylight saving settings when using external time controller.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Per_Sjöstrand
    Per_Sjöstrand
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
966 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Daylight saving settings when using external time controller.

Picard Product_Support
‎2018-09-06 02:57 PM

Issue

Daylight saving (DST) settings when using external time controller.

Environment

  • Vista Server
  • NTP External Time Controller

Cause

Sometimes customers prefer to use an external software and/or device to monitor and set the actual time in the computer, sometimes it also controls the daylight savings.

Resolution

When using TAC Vista servers in a network with an external time server (e.g. connected to the TAC Vista master server) it might be a good idea to switch of the daylight saving and only use standard time. The daylight saving/standardtime is controlled by the events, $Summer and $Winter. They can be changed in the property menu for the server object.

  1. First, make sure that all computers don’t have the checkbox “automatically adjust clock for daylight savings” checked in the date and time property dialog, with this box unchecked, TAC Vista controls the daylight savings on the computer.
  2. You also need to set TAC Vista in standard time status (if it isn't already).If it is, go to the properties menu on the server object, Time control. Make sure that “daylight saving difference” is changed from 60 min to 0 min. Then go to the daylight savings menu and uncheck the start and stoptime to make sure that the event doesn’t run next time. Do the same thing in the standard time menu.
  3. If you’re in daylight savings mode already, you have to run the standard time event. Do this by selecting weekday and month. e.g. third Wednesday in April. Change the start time to a couple of minutes later, press ok and open the properties dialog again to make sure that next event is happening soon. Check the state in the properties menu on the server object, Time control, it should be standard time now. Now do the settings mentioned in chapter 2. By doing this the external time server now can control time and daylight savings in the TAC Vista network.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 2660
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of