Damaged or Disabled Licenses

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Damaged or Disabled Licenses
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
13342 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Damaged or Disabled Licenses

Picard Product_Support
‎2018-09-10 10:12 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:49 AM

Issue

Licenses are becoming damaged repeatedly over time and/or licenses are going in to a disabled state.

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • SmartStruxure
  • License Administrator
  • Virtual Machine

Cause

Damaged Licenses: If the license server / license administrator is installed on a virtual machine, the common reason for damaged licenses is that the MAC address of the virtual machine is not set to be static. Every time the MAC address changes, the license will become damaged.

Disabled Licenses: This is usually caused when the license fails to complete a process such as a return or repair. This could be due to an intermittent internet connection or the process timed out while trying to communicate with the license server.

Resolution

Repair License with License Administrator

The first step to take with a damaged or disabled license is to use the repair function in license administrator. Follow the steps from WebHelp topic Repairing an EcoStruxure Building Operation Software License. If the repair function does not work, then the license server will need to be reset. 


Reset License Server (Unable to Repair License)

Below are the steps to remove the damage or disabled licenses before reactivating the permanent licenses again:

  • Put a SBO demo license on the site to get it back up and running right away.
  • Locate the Entitlement ID and/or activation ID of the impacted licenses. Open a case with your local BMS support group and provide them this information. This information will be used to release the licenses to prepare them to be rehosted.
  • There are then two potential methods to  reset the license server:
    1. Download and run the SBO License Server Reset tool from the Community
    2. Manually reset the License Server
      • Stop the License Server.
      • In the License Server application folder, remove all files:

                - File path for Windows 7, Windows 8.1, and WIndow 10: \ProgramData\FLEXnet

                - File path for Windows Server 2008 and Windows Server 2012: \ProgramData\FLEXnet

 

      • Start the License Server
      • Reactivate the returned network licenses.

 

Note: When you reactivate all returned network license, new License Server .data files are created together with the activation of the first license. For more detail, reference WebHelp: Resetting the License Server.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (15)
  • Find more articles tagged with:
  • 19459
  • asp
  • automation
  • broken
  • CraigEllis20
  • enterprise
  • GaryMontague23
  • HernanUruena25
  • locked
  • manually
  • PeterLarsen20
  • PeterLarsen21
  • PeterLarsen22
  • relinquish
  • workstation
Was this article helpful? Yes No
90% helpful (9/10)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore