Issue
Using Download Wizard 32 with Application set to Clear Memory, one will get an error that "The application file could not be found!
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Workstation
- Xenta Programmable Controller
Cause
EBO Workstation does not include the Lonm<Model Number>.MTA file.
Resolution
There are two solutions:
- Create a minimal MTA file for the device type.
- Open Menta Editor
- Change the device specification for the appropriate Xenta Type.
- Add one PVR block
- Save the file.
- In DWiz, change Application selection to Download New and Browse in the new file.
- Perform the steps again with the expected files in the same folder as DWiz.
- Download the attached Lonm.zip (derived from Menta 5.1.9)
- Extract the files in the zip to the same Workstation folder where Dwiz.exe is found. Sample Location: "C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation 3.2\WorkStation\DWiz.exe"
- Perform the download again with the same Clear Memory selection under the Application section.