Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DUIC-5P-12V Digital Input Expander and use with SpaceLogic Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • DUIC-5P-12V Digital Input Expander and use with SpaceLogic Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1211 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DUIC-5P-12V Digital Input Expander and use with SpaceLogic Controllers

RandyDavis Champion
‎2025-06-30 12:04 PM

on ‎2025-06-30 12:04 PM

Issue

Programming for the use of Smartware Technologies DUIC-5P-12v input multiplexer

Product Line

TAC IA Series, EcoStruxure Building Operation

Environment

  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation RP-V VAV
  • Building Operation Room Controller
  • I/A Series N4 Jace 8000/9000
  • I/A Series N4 Enterprise Server
  • Building Operation Automation Server Premium

Cause

Define the application programming and configuration of the DUIC-5P-12V in various enviroments using SpaceLogic contollers

Resolution

The DUIC-5P-12V Card allows for conversion of a single universal input channel to accept up to
five voltage free contacts of any mixture such as mercury wetted, Triac, etc., which may have
inherently large and varying resistances. The DUIC-5P-12V on-board circuitry allows the
controller inputs to have a consistent input reading, unaffected by long lead lengths, varying
resistances, etc. 

  • Smartware Technologies Documents includes programming for use in SpaceLogic devices under an AS-P in the form of a Function Block program.
  • When SpaceLogic controllers are used in the Niagara Frameworks Jace 8000/9000 or hosted directly under a Niagara Frameworks Enterprise Server, the programming is done in a Visual Script Programming format utilizing the Schneider MPX modules in Workbench.
  • The documentation addresses the original use for the I/A Series MNL and MNB contollers as well.
  • NOTE:  The device requires half wave 5 -12 DC or 24 VAC only to prevent damage
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Attachments
DUI_App.zip
DUIC-5P Software EBO.zip
Tags (1)
  • Find more articles tagged with:
  • RandyDavis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore