DPUs stopped letting people through doors after upgrading the site from I/NET 2000 to the latest revision of I/NET Seven
  • DPUs stopped letting people through doors after upgrading the site from I/NET 2000 to the latest revision of I/NET Seven
  • sesa139513
    sesa139513
‎2018-09-06 03:21 PM
I/NET site with Access Control
  1. Using Dbcreate, select “Verify existing database” and start the process. You will probably find errors or differences listed at the end of the verification check. (This probably caused the crash.)
  2. Using Dbcreate, select “Upgrade database” and start the process. Force I/NET Seven to upgrade the system. (The upgrade will attempt to repair the differences.)
  3. Once again, “Verify existing database” the database using Dbcreate. There should be “0” (zero) differences. If there are no differences, then the database is ready to be used in I/NET Seven.
  • TAC INET
  • 1329