DDC Lines show only inconsistently when viewed through a Xenta 527 Web Server Graphic
  • DDC Lines show only inconsistently when viewed through a Xenta 527 Web Server Graphic
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 01:04 PM
I/NET
Xenta 527 5.1.3 and below
Issue corrected in 5.1.4 release
  1. Upgrade the Xenta 527 to the latest revision of I/NET or at least 5.1.4
  2. Upgrade Xbuilder to the exact same revision
  3. Send the upgraded project files to the upgraded controller.