Issue
DC1100 / DC1400 Outside Occupation message is displayed and Plant is not operating.
Environment
DC1100 / DC1400 Discrete Controller.
Cause
Heating Time Schedule is in an OFF period.
Remote Override has been activated.
Controller Current Time is incorrect.
Room Sensor does not display a value or is not listed.
Resolution
-
Check Heating Time Schedule OFF time.
- If Heating Time Schedule OFF time is earlier than the Controller Actual Time then condition displayed is correct.
- If Heating Time Schedule OFF time is later than the Controller Actual Time then condition displayed is incorrect.
-
Check presence of Drayton DC1100 Remote Switch Unit.
- This can be confirmed by presence of wire connected to Controller Terminal 9.
- Check / amend setting of Drayton DC1100 Remote Switch Unit in order to test accuracy of message displayed.
-
Check presence of bespoke Remote Override Control Unit
- This can be confirmed by presence of wire connected to Controller Terminal 9.
- A 33K Resistor should also be visible wired between Controller Terminal 9 and Terminal 7
-
Check / amend setting of Remote Override Control Unit in order to test accuracy of message displayed.
- N.B.
- The Drayton DC1100 Remote Switch Unit is common to both DC1100 and DC1400 installations.
-
If the DC1100/1400 is used as an Optimiser, check the room sensor is connected and reading.
- Rectify the issue, a coldstart may be required to reconfigure the controller.