DC1100 / DC1400 Optimiser / Compensator Controller switched contact output compatibility with existing Boiler / Pump / Control Valve Actuator control circuits.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • DC1100 / DC1400 Optimiser / Compensator Controller switched contact output compatibility with existing Boiler / Pump / Contro...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3464 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DC1100 / DC1400 Optimiser / Compensator Controller switched contact output compatibility with existing Boiler / Pump / Control Valve Actuator control circuits.

Picard Product_Support
‎2018-09-10 03:07 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM

Issue

DC1100 / DC1400 Optimiser / Compensator Controller switched contact output compatibility with existing Boiler / Pump / Control Valve Actuator control circuits.

Environment

  • Stand alone Optimiser / Compensator Controller
  • CMC1801
  • CMC1802
  • CMC1803
  • CMC1826
  • CMC3803
  • CSMC3804
  • CSMC3805
  • DC1100
  • DC1400
  • Contacts
  • Output

Cause

DC1100 / DC1400 Optimiser / Compensator Controller is to be connected to existing Boiler / Pump / Control Valve Actuator control circuits previously connected to Satchwell CMC or CSMC Optimiser / Compensator Controller.

Resolution

IMPORTANT NOTE

Satchwell CMC / CSMC Controller output contacts are VOLT FREE.

S-E Satchwell DC1100 / DC1400 Controller output contacts are LIVE MAINS VOLTAGE.

It may therefore be necessary to install Relays between the DC1100 / DC1400 outputs and any Plant Control Circuits / Control System Devices under control.

For example, where a 24v Valve Actuator was originally controlled via volt free contact outputs of a CMC / CSMC Controller then the Actuator may now need to be controlled via live mains voltage contact outputs of a DC1400 Controller.

A 230v coil Relay will therefore need to be connected to the Valve Open contact output of the DC1400 Controller while another 230v coil Relay is connected to the Valve Close contact output of the DC1400 Controller.

The 24v power to drive the Valve Actuator Open and the 24v power to drive the Valve Actuator Close should then be connected to the Valve Actuator via the contacts of the appropriate Relays.

Should the 24v power source originally have been provided by the CMC / CSMC Controller and no other 24v power source is available on the existing installation then this may be remedied by the installation of a S-E TR 230/24v Transformer.

N. B.

Normally a Satchwell CMC or CSMC Controller would be replaced by a S-E Satchwell DC1400 Controller in order that existing Satchwell Sensors may be retained for connection to the DC1400 Controller.

In the event that a Satchwell CMC or CSMC Controller should be replaced by a S-E Satchwell DC1100 Controller then any existing Satchwell Sensors will also need to be replaced.

DC1100 Overview details appear here.

DC1100 Wiring and Commissioning details appear here.

DC1400 Overview details appear here.

DC1400 Wiring and Commissioning details appear here.

TR Transformer details appear here

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6123
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.