Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Creating a standard graphic in Vista 5

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating a standard graphic in Vista 5
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Per_Sjöstrand
    Per_Sjöstrand

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1686 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating a standard graphic in Vista 5

Picard Product_Support
‎2018-09-07 01:56 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-25 11:30 AM

Issue

The standard graphic object does not exist in Vista 5 the same way it did in previous versions so an alternative method for creating a standardized graphic is necessary.

Product Line

TAC Vista

Environment

  • Vista Workstation
  • TGML Graphics

Cause

The standard graphic object does not exist in Vista 5 as it did in earlier versions. Relative bindings and shortcuts replicate the functionality of having one graphic source file represent data from several different pieces of equipment.

Resolution

There are a couple of alternative methods to creating a standardized graphic that will work where many identical or similar devices exist. Below is an example of the first method. The scenario is a site where multiple Xenta 121 devices exist and each need individual graphics.

  1. In Vista Workstation locate the first Xenta 121 device in the folders pane on the left and right click and select New > Object > Graphic - TGML to create a new graphic that resides in the controller object.

    Step 1.png

     

  2. Create a standardized graphic that uses naming conventions that are common to all of the devices that will use the graphic. In the example the actual SNVT names from the Xenta 121 are used for the point names.
  3. When the graphic is complete, save it and create the graphic bindings to the controller where the graphic resides.

    Step 3.png

     

  4. From the bindings pane select all of the bindings then right click and select Apply Relative Address.

    Step 4.png

     

  5. The addresses on the bindings will now only contain references to the points within the controller but will not have any reference to the controller name as shown below.

    Step 5.png

     

  6. Close the bindings window and right click the graphic object and select copy.

    Step 6.png

     

  7. Right click on the next device and select Paste Shortcut. Repeat this step for all of the relevant devices.

    Step 7.png

     

  8. Now, clicking on the shortcut to the graphic from any of the devices will open up a copy of the graphic that is bound to the device in which the shortcut resides.

The other is similar but places all of the shortcuts to the graphics in individual folders rather than down in the devices. It also requires that shortcuts be made in the folders to each of the devices.

  1. Create a graphic (use this graphic as a standard graphic) with relative bindings.
  2. Create folders for e.g. every room.
  3. In this folder, add shortcuts to the controllers, also add a shortcut to the graphic (with the relative bindings).
  4. By doing this you can have the function of "TGML standard Graphics" as in earlier OGC graphics.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 2574
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore