Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Create smooth rotation for an object in a TGML graphic

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Create smooth rotation for an object in a TGML graphic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa150555
    sesa150555

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2552 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Create smooth rotation for an object in a TGML graphic

Picard Product_Support
‎2018-09-07 12:40 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-25 11:09 AM

Issue

Create smooth rotation for an object in a Vista TGML graphic

Product Line

TAC Vista, EcoStruxure Building Operation

Environment

TGML Graphics Editor

Cause

If the "CalcMode" is set to "Discrete" the object will rotate the full specified range instead of taking the duration time to slowly move around it. 

Resolution

rotate.png

  1. Add a <rotate> tag to the object that will be rotating.
  2. Add an <animate> tag to the rotation.
  3. Set the properties for the animation:
    1. Animation = default state (Start/Stop), if a binding is ultimately used to control when the animation occurs, bind to this attribute.
    2. AutoReverse = should the animation continue in one direction or get to the end of the animation and then come back to the beginning? (True/False)
    3. CalcMode = determines whether the animation is smooth or jumps from end point to end point of the animation. For rotation, choose Linear. (Linear/Discrete)
    4. Duration = the amount of time in seconds that the animation should take. Higher numbers result in slower animation.
    5. Freeze = if true, the animation will pause at the last position when Animation is set to False. Otherwise it will revert back to the starting position. (True/False)
    6. Repeat = how many times should the animation occur. Default value is "Forever" but this value can also be set to any integer number (1, 2, 3, 4...)
    7. From, To = depend on the desired animation and target attribute. For rotation 0 to 360 is typical.
    8. Attribute = for rotation, the Angle property of the <rotate> tag is animated from 0 to 360 degrees.

For more information on CalcMode see ‘Animation Overview’ in the Help.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 2510
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore