Could an TAC Xenta 421-A device send out SNVT values with engineering values?
  • Could an TAC Xenta 421-A device send out SNVT values with engineering values?
  • MikaelKrantz
    MikaelKrantz
‎2018-09-06 09:14 AM
Last Updated: Administrator DavidFisher Administrator ‎2019-07-09 09:03 AM
When TAC Xenta 421-A is used as stand alone LonWorks node, a value read from an 0-10 VDC or 4-20 mA is sent only as 0-100%. Is it possible to send as engineering values?
EcoStruxure Building Operation,TAC Vista
TAC Xenta 421-A
Then the TAC Xenta 421-A is used as a stand alone LonWorks nodes, the values from an analog input is always sent as nvoAnalog1-4, in 0-100%.
Only exception is then using thermistor inputs, when the measured temperature is sent out as nvoTemp1-4.
TAC Xenta 421-A used as stand alone LonWorks node, the values from an analog input is always sent as nvoAnalog1-4, in 0-100%, unless the input is configured from 1.8 kOhm or 10 kOhm thermistors..