Converting a NL220 database to LonMaker

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Converting a NL220 database to LonMaker
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1945 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Converting a NL220 database to LonMaker

Picard Product_Support
‎2018-09-11 04:34 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:37 AM

Issue

How to convert a NL220 database into a LonMaker database.

Environment

  • NL220
  • LonMaker
  • LNS

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

There are a number of steps that must be taken to convert a NL220 database to LonMaker. 

Resolution

Note: Before beginning this process make sure that the NL220 database has all devices underneath one root system (In this example, everything was moved into the InfraStructure root system). If this is not done, the controllers will not appear in the LonMaker Visio drawing. Make a backup of the NL220 database before doing anything else.
 

  1. Create a new LonMaker database and open it up (For this example it was named NLtoLM). Note: You do not need to register any plug-ins or go OnNet at this time.
  2. Now close the LonMaker project. 
  3. Go to the location of the NL220 database and copy all of the folders and files in the database that you want to convert. In most cases you can find the database files here; C:\NLprj\PROJECT NAME.
  4. Go to the location of the LonMaker database that you just created and delete all of the files located in the project folder. In most cases it will be located here; C:\Lm\DB\PROJECT NAME.
  5. Paste the project folders and files from the NL220 database into the LonMaker database folder.
  6. Now go back to LonMaker and create the Visio drawing for the new LonMaker database. Make sure to select the project you created in the Drawing directory field and to select "" in the Drawing name field. Click Create Drawing.
  7. You may get a Database error. Click OK.


    The LonMaker database has now been created with the Visio drawing. The drawing may be a mess and will require additional time to move nodes around and clean up the appearance of the database. If there are subsystems in the project it will create each subsystem layer in a separate Visio drawing. In order to combine the subsystems back into one drawing follow steps 8 through 13.
     
  8. On the main Visio drawing, click and drag a new subsystem to the Visio drawing. Give the new subsystem a name that is not used in the database.

  9. Go to the subsystem that you want to move and select everything on the page. Right click and go to Move Device > Change Subsystem...
  10. Navigate to the new subsystem that was created in step 8 and click OK. Repeat steps 8 through 10 for each subsystem you want to move.
  11. Go back to the main Visio drawing and delete the original subsystems that were on the page.
  12. Now the new subsystems can be renamed to the original subsystem names by right clicking and going to Properties.
  13. You now have one LonMaker Visio drawing for your entire database.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 13909
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore