Converting 7791/7792 MCI Controllers To 7793

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Converting 7791/7792 MCI Controllers To 7793
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1738 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Converting 7791/7792 MCI Controllers To 7793

Picard Product_Support
‎2018-09-06 03:12 PM

Issue

I/NET Seven does not support the 7791/7792 MCI platforms. Only the 7793 MCI platform is supported. Consequently, a conversion from the 7791/7792 MCI platforms to the 7793 MCI platform is necessary. The following steps should insure a correct conversion.

Environment

7791/7792 MCI platforms

Cause

I/NET Seven does not support the 7791/7792 MCI platforms. Only the 7793 MCI platform is supported.

Resolution

A Hand Held Console (HHC) is required for this process.

  1. Turn EVERY sub-LAN device “Internal” using the MCU Configuration Editor under Edit > Controller > MCU Configuration.
  2. Save the current databases in the MCIs (7791/7792).
  3. Attach the Hand Held Console (HHC) to a MCI. Use the following keystrokes to clear the MCI memory:
    • CTRL, MEM, ENTER, “0”, ENTER.
    • Press the red RESET button on the MCI
    • The indication on the HHC should be seconds counting up from zero.
  4. Using the HHC, enter CODE, 90, and press the ENTER key.  The display should show the current MCI configuration (i.e., 7791 or 7792 and TAP emulation of 01, 03 or 06). 
  5. Using the increment/decrement keys advance the display to show 779301 or 779306 (use the –06 if dialing into a MCI with the RS-232 Expansion board attached--otherwise use the -01) and press the ENTER key.  The display should indicate seconds counting up from zero. 
  6. Check the COMM port speed on the MCI using the HHC.  Enter in CODE, 91, and press the ENTER key.  The display will show the COMM port speed, typically 19,200 if directly connected to a PC.  Change the port speed using the INC key to 19200 if necessary.
  7. Move the I/NET 2000 saved databases (DCUXXXX.sav) to the SAV folder in I/NET Seven.
  8. In I/NET Seven connect to the Link address where the MCI is located.  Go to Edit > Host Computer > Software Restore, and check the MCI address to download the .BIN file only (do not load the .SAV file here). 
  9. After the .BIN file downloads to the 7793, connect to the MCI.  Go to Edit > Controller > Station Restore, and download the .SAV file to the controller.
Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 1749
  • 77917792
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore