Convert existing Idisc to large numbers (Hex)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Convert existing Idisc to large numbers (Hex)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa139513
    sesa139513
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2354 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Convert existing Idisc to large numbers (Hex)

Picard Product_Support
‎2018-09-07 12:11 AM

Issue

Convert Key Card Translation table to a Large Number and then remove the Key Card Table entry from I/NET.

Product Line

TAC INET

Environment

I/NET site with Access Control

Cause

The process described will allow you to do this conversion on an active system without causing the Idisc to fail during process.

Resolution

For example take the Key card translation table below:

key-card-translation.png

With this Individual editor:

individual-editor.png

Make an excel spread sheet that performs this calculation multiple times, or you can do it one at a time manually. The information needed for this calculation is located in the Key Card Table and Individuals editor.

  • Source Number (from Key card table)
  • Individual Number (from Individual editor)
  • Target Number (from Key card table)
  • Decimal Number (from Individual Editor)

Source Number + Individual Number - Target Number = Decimal Number

Source Number Individual Number Target Number Decimal Number
67806444 00001 1 67806444
67806444 00002 1 67806445
67806444 00003 1 67806446
67806444 00004 1 67806447
67806444 00005 1 67806448

 

  1. Go into the Individual editor and modify an individual entry
  2. Take the calculated decimal number from the calculation above and add it into the Decimal Number area.
    decimal-number-field.png
  3. The I/NET program will calculate the Hex number automatically. This Hex number should be the same as the bottom of the Idisc itself.
    Note: ONLY delete the Key table lines after you completed the entire tenant conversion. This will insure that all people will get into and out of the building.
    Note: These changes can be done on an active system.

This is the process of adding NEW people in the system that has existing Key Card Translation table and you want to enter the NEW Disk as large numbers.

  1. Go into the access Individuals editor and Add a new person.
    skipped-individual-number.png
  2. It is not permitted to back-fill any existing Individual Numbers. In the example above Individuals 00001, 00003, and 00004 are defined. It is not possible to add Individual 00002.
    Go to the end of the Individuals list and choose the last number + 1 number.
  3. Set the Individual Number then place the cursor on the middle box and touch the new disc to the wand. This will place the Hex number in that box from the Idisc.
    add-individual.png
  4. The Hex number and Decimal number are listed in the Individual Parameters.
  5. Complete the process by filling out the rest of the Individuals editor.
Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 1996
  • idisk
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore