Controlling a PWM transducer using Xenta 102-AX PWM_1 output

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Controlling a PWM transducer using Xenta 102-AX PWM_1 output
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Trey_Boothe
    Trey_Boothe
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1059 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Controlling a PWM transducer using Xenta 102-AX PWM_1 output

Picard Product_Support
‎2018-09-06 02:48 PM

Issue

The Xenta 102-AX PWM_1 (one output PWM) setting is a true duty cycle output.  How can you control a PWM transducer?

Environment

Xenta 102-AX, Universal Output 2

PWM Transducer

Cause

The problem is that 0% on a duty cycle output is no pulse at all and 100% is continually on. All electronic transducers must have some pulse to control it to 0%, often 0.1 seconds. Many of them will not accept a continually on signal as 100%.

Values for two of the most industry common PWM transducers are detailed below.  Calculations provided can be used to calculate any required duty cycle limits.

Resolution

This example assumes a PWM transducer that requires a pulse width modulated signal between 0.1 and 5.2 seconds.

  1. Set the stroke time to a value slightly larger than the required maximum pulse.
    UnivOut2_Object.SCPTdriveTime = 5.3 seconds
  2. Set the minimum range to a percentage of the drive time that will result in a 0.1 second pulsed output.
    UnivOut2_Object.nviUnvOutput2.SCPTminRnge = 1.885%
    0.01885 * 5.3 = 0.099905 seconds
  3. Set the maximum range to a percentage of the drive time that will result in a 5.2 second pulsed output.
    UnivOut2_Object.nviUnvOutput2.SCPTmaxRnge = 98%
    0.98 * 5.3 = 5.194 seconds
  4. Set the minimum pulse to 0.1 second.
  5. A 0-100% signal on Universal Output 2 will now modulate the pulse width between 0.1 and 5.2 seconds.

This example assumes a PWM transducer that requires a pulse width modulated signal between 0.1 and 25.6 seconds.

  1. Set the stroke time to a value slightly larger than the required maximum pulse.
    UnivOut2_Object.SCPTdriveTime = 25.7 seconds
  2. Set the minimum range to a percentage of the drive time that will result in a 0.1 second pulsed output.
    UnivOut2_Object.nviUnvOutput2.SCPTminRnge = 0.39%
    0.0039 * 25.7 = 0.10023 seconds
  3. Set the maximum range to a percentage of the drive time that will result in a 25.6 second pulsed output.
    UnivOut2_Object.nviUnvOutput2.SCPTmaxRnge = 99.61%
    0.9961 * 25.7 = 25.59977seconds
  4. A 0-100% signal on Universal Output 2 will now modulate the pulse width between 0.1 and 25.6 seconds.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 3036
  • pwm1
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of