Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Control a dual duct VAV box with Xenta controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Control a dual duct VAV box with Xenta controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2519 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Control a dual duct VAV box with Xenta controllers

Picard Product_Support
‎2018-09-06 03:04 PM

Issue

How can I control a dual duct VAV box with Xenta controllers?

Environment

Xenta 102-AX

Dual Duct heating/cooling

Cause

The Xenta 102-AX is an application specific controller designed to vary the volume and outlet temperature of a single terminal unit. It does not, by default, control a dual duct, where a constant source of cold air and hot air and delivered in separate ducts.

Resolution

You could conceivably use a single Xenta 102-AX with the airflow pickup on the discharge of the box instead of the inlet. Then connect the hot deck damper as a 2-out PWM heat stage.

A more elegant solution is to use a pair of Xenta 102-AX controllers. One 102-AX is connected to the cool deck and setup normally. Either its heating airflow setpoint is set to match the cooling low flow or heating airflow is set to 0 if you wish the cool deck to shut off in heat. The "Effective Setpoint Source" must be set to "Norm of Heating and Cooling Setpoints" so that the setpoint sent to the hot deck controller will not bounce from heating to cooling when room conditions change. For this reason, it might be preferable to use an STR-202 so that there is no digital display to confuse the occupant.

The second 102-AX is connected to the hot deck, space temp is bound from the first and nvoeffectivesp is bound from the first to nvisetpoint of the second. Configure input 1 as a duct temp and connect a 4.7Kohm resistor from it to ground. This will simulate a duct temp of 110°F and keep it in warmup mode. As with the cool deck, you have a choice whether to set the warmup low flow to 0 or to some minimum position. Set your occupied setpoints to the same values as the cool deck controller. (It's actually using them in the setpoint calculation, but for simplicity's sake, set them the same. For a more complete description, consult the reference manual concerning nviSetpoint.)

You should also bind nvoOccupancyStatus from the cool box to nviOccCmd on the hot deck box. That way if someone puts the box in to after hours override, they'll both operate.

As mentioned before, the room sensor (STR-200/202/250) is connected to the cooldeck controller. You'll need to connect 3 conductors to a 1/8"TRS jack to the hotdeck controller in order to connect the MSTAT for calibration purposes. Otherwise you'll have to crawl into the ceiling to connect it.

This arrangement is based on having airflow sensors on the inlets of both the cold and hot deck.

Labels (1)
Labels:
  • TAC Vista
Tags (4)
  • Find more articles tagged with:
  • 2088
  • double
  • morning
  • thermostat
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore