Continuum analyzer errors in IETableCheck.
  • Continuum analyzer errors in IETableCheck.
  • AbeMeran
    AbeMeran
‎2018-09-06 01:35 PM
Continuum analyzer reports errors in the IE Table Check.
Cyberstation
Errors need to be cleaned up using the Continuum analyzer.
  1. Clean up the errors using the Continuum analyzer then run the tests again to verify errors where corrected.
  2. If everything appears to work correctly then there is no need to reload the IE table to the controllers, otherwise:
    1. Send the IE table to CX level controllers.
    2. To send only the IE table select the 'Do not reload attached objects' in the 'Send To Controller Options' dialog window.