Continuum BCX controller password reset

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum BCX controller password reset
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
11458 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum BCX controller password reset

Picard Product_Support
‎2018-09-10 06:27 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:56 AM

Issue

Is there a way to reset the password for web access to a BCX?

Product Line

Andover Continuum

Environment

Continuum site with passwords other than the default

Cause

The password was changed by mistake.

Resolution

Restore the controller's user names, passwords and configuration settings to the original factory values (Reset IP button using a two stage operation) The location of the Reset button and the Reset IP button on the controller board. Page 124 in appendix A of the Technical Reference Guide.

If you cannot get into Continuum Explorer and edit the controller user under that controller and set the password. You will have to reset the controller and then re-commission and then reload.  Try acc/acc first and then after that the following:

Using the Reset IP button

The Reset IP button has two stages of operation:

  • Stage 1 is initiated by depressing the button for 5 seconds. After 5 seconds, the IP address, and all network-related addresses entered on the Network Configuration page, are returned to the original factory default values.
  • Stage 2 is initiated by depressing the button for 35 seconds. After 35 seconds, the database is cleared and all persistent configuration data is erased, with the exception of the error log.

Note: Depressing the button for 35 seconds performs both operations, setting the IP address back to the factory default setting and clearing the database.

When you initially depress the Reset IP button, the CPU Indicator LED will begin blinking. At 5 seconds, the LED will stop blinking and remain lighted in a continuous state.

If you release the button before 5 seconds has passed, no changes are made.

If you release the button after 5 seconds, but before 35 seconds, stage 1 is executed, but stage 2 is not. The IP address has returned to the original factory value, but the database has not changed.

Please see Default IP address for BCX, ACX57xx, CX9702 and Netcontroller II for information on default IP addresses.

Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (1)
  • Find more articles tagged with:
  • 7790
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore