Issue
Continuum BACnet devices not seen in Continuum Explorer
Environment
CyberStation
Cause
"Continuum Explorer\View\Show Continuum BACnet Devices As" is set to "Infinet Controllers only"
Resolution
"Continuum Explorer\View\Show Continuum BACnet Devices As" is set to "Infinet Controllers only"
Set to "Infinet Controller and BACnet Device
The slightly confusing thing is that all Non Continuum (third party) devices still appear in the Bacnet view. This is correct, as designed. See below for both examples