Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Continuum BACnet controllers are sending out incorrect or large amounts of unnecessary COV data on the network.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum BACnet controllers are sending out incorrect or large amounts of unnecessary COV data on the network.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa101527
    sesa101527

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1343 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum BACnet controllers are sending out incorrect or large amounts of unnecessary COV data on the network.

Picard Product_Support
‎2018-09-06 03:02 PM

Issue

Continuum BACnet controllers are sending out incorrect or large amounts of unnecessary COV data on the network.

Environment

Continuum BACnet controllers

Cause

The Continuum BACnet controllers cannot be programmed the same as the Non BACnet Continuum controllers when it comes to points that are being exported to other controllers. There are 2 main differences that the programmer must be aware of when programming these exported points.

Resolution

The first difference to be aware of is that in a Continuum BACnet controller every change of the value of an exported point is immediately sent out at the time of the change regardless of when the point changed within the controller program scan. What this means is that unlike standard continuum programming which latches and exports the final value of a point after the entire controller scan is completed, the Continuum BACnet controller will send out any change it sees during the scan. So if you were toggling a point's value several times within the same program or within multiple programs, all the changes to the value are sent to recipient controllers during the scan, not just the final value. This will cause both incorrect and unnecessary data exports.

The second difference is that, in the case of standard Continuum points such as InfinityNumerics and InfinityOutputs, some values can be sent to them that are not reflected directly when the values are translated into BACnet. For example if you had an InfinityNumeric and used it as a binary value in the BACnet world, a program could set it to "On" and later in a program you may perform Boolean logic on it and it would be set to a logical "1", or "true". In the Standard Continuum, these values would be different, however in BACnet, both of these values would be translated to the same value. Because the evaluation of the COV point change is done before we translate it to the BACnet standard we would transmit this as a change of value even though the value transmitted in both cases would be the same. In this case we would transmit the COV during the scan every time we saw this value toggled to what BACnet would think was no change. This would cause unnecessary COV data to be transmitted.

The bottom line is that if you, through "Plain English" need your logic to set a value to a Continuum BACnet object more than once during the program scan and it is being exported, you will need to use an intermediate point such as a local variable or an InfinityNumeric to store the changes and only commit the final value to the exported point at the end of the manipulation.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2169
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore