Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Continuum Alarm Process with Enhanced Alarm Logging enabled

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum Alarm Process with Enhanced Alarm Logging enabled
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • ScottLeedberg
    ScottLeedberg
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2397 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum Alarm Process with Enhanced Alarm Logging enabled

Picard Product_Support
‎2018-09-06 03:03 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-26 08:29 AM

Issue

How does a controller get an alarm into the database when using the Enhanced Alarm Logging feature of CyberStation?

Product Line

Andover Continuum

Environment

Cyberstation

Cause

Continuum Alarms are configured in the Netcontrollers and Infinet-controllers at each site. Only the CX Controller sends alarms to the Cyberstations once a point in the Controller surpasses its threshold and goes into an alarm state. The CX Controller then uses an internal algorithm to determine which CyberStation will log the alarm.

Resolution

  1. The alarm is sent to the first (Non "0" Network ID) Cyberstation on its list of known devices.
  2. If the controller does not get a response from this workstation that the alarm was logged, it will try again three more times.
  3. If the workstation still does not respond to the controller, the controller will flag this workstation as offline in its internal controller database.
  4. It will then move to the next workstation in its list until it finds a workstation that is online and has logged the alarm successfully.
  5. If no workstations respond to the controller, the controller will buffer the alarm internally until it can find a workstation that is online.
  6. If the workstation is online, the alarm will be logged to the Continuum Database and then the database will notify the Workstation that the alarm was logged successfully.
  7. When the workstation gets this notification from the database that the alarm was logged, it will in turn send a notification to the CX controller that the alarm was logged successfully.
  8. Next, the controller will send the alarm to all recipient workstations for this alarm. When the controller is sending the alarm to the other recipient workstations it will follow the same logic and try to send it three times to each.
  9. If for any given recipient workstations the controller does not get a response that the alarm was received the controller will flag that workstation as offline internally and not try to send the alarm to that workstation again.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2109
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore