Issue
Connection to a DMS MicroPlex MSC-NC is successful. However, when accessing a networked MicroSmart controller, the connection attempt fails.
Environment
- DMS MicroPlex MSC-NC
- MicroSmart Controller
Cause
Flash ROM in the MSC-NC
Resolution
Reload of the flash in the MSC-NC:
- Power down
- Jump J1 (near processor)
- Power up.
- Connect with DCT
- Remove J1 jumper f. Do “Alt-L” as this will start installation of Flash ROM.
The above will also take care of these problem issues:
- Back door password (lack of)
- "Ghost" controllers that are not there
- None standard service alarm code (sample: 44+service alarm44144144/144)