Connecting a SpaceLogic Controller via MSTP

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Connecting a SpaceLogic Controller via MSTP
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
7 Likes
6482 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Connecting a SpaceLogic Controller via MSTP

Sisko GavinHe Sisko
‎2022-12-08 05:25 PM

Issue

How to connect a SpaceLogic IP Controller via MSTP

Product Line

EcoStruxure Building Operation

Environment

  • Workstation
  • Automation Server (ASP/ASB)
  • Space Logic IP Controller
  • RS-485 Adapter

Cause

Only certain SpaceLogic IP Controller models and versions support the new BACnet MSTP Adaptor and details are required on how to configure these controllers for BACnet MSTP.

Resolution

The following video will illustrate how to:

  • Configure ASP/ASB for BACnet MSTP Communication.
  • Configure a SpaceLogic IP Controller as a BACnet MSTP device.
  • Discover the SpaceLogic IP Controller on the BACnet MSTP network.

Things you need:

  • Software
    • EcoStruxure Building Operation Workstation 2022
    • Building Commission Application (available from Google Play, Apple Store, or Microsoft Store)
  • Hardware
    • ASP/ASB version 4.0 or higher
    • RP controller (hardware version 10 )
    • RS-485 Adaptor (Isolating or Non-Isolating)
    • RJ45 UTP Straight Through Cable (12"/300mm or less)
    • Note: - if the RP controller does not show MSTP settings check the Space Logic IP controller firmware release notes and install firmware corresponding to the EBO version.  For example firmware versions 3 and below do not have settings for MSTP configuration.
  • Before attempting to install a SpaceLogic controller on MSTP consult the following:
    • Isolated RS-485 Adapter and Non-isolated RS-485 Adapter for SpaceLogic IP controller types supporting the RS-485 MSTP adapter
    • RP-C BACnet MS/TP Support for RP models supporting BACnet MS/TP
    • Installing an RS-485 Adapter for information on installing the BACnet MSTP adapter
    • Connecting an Isolated RS-485 Adapter and Connecting a Non-isolated RS-485 Adapter for port usage and CAT 5 UTP connection cable
    • Allocating Flexible Ports for additional considerations on port usage
    • Enabling the BACnet/IP Controller to Communicate on an MS/TP Network

Please see the video below:

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • GavinHeward22
  • GavinHeward25
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore