Configuring a RS-232 Sigma field connection between a controller and laptop
  • Configuring a RS-232 Sigma field connection between a controller and laptop
  • CraigEl
    CraigEl
‎2018-09-07 11:18 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-07 04:41 PM
Unable to establish communication between a Sigma laptop and a Sigma controller via the RS-232 connection (Diagnostic Port SK1).
Satchwell BAS & Sigma
Sigma UNC Controller
Incorrect configuration settings.
Use the following checklist to verify and correct the configuration:
On the Main Sigma Server
  • ✅ Create a Service Server in the main Sigma server.
  • ✅ Ensure Att.set files are downloaded to the controllers.
On the Laptop
  • ✅ Edit the configuration file located at C:\\Sigma\\Data\\Sigma.ini:
    • Set RS232 = 1
    • Set Commport = 1, Baudrate = 9600
      ⚠️ Note: Ensure the BAS Integrator is disabled, as it defaults to Comm Port 1.
  • ✅ Set the Laptop Server Number to match the Service Server Number configured in the main server.
    (Navigate to: System Setup → General → Server Details)
  • ✅ Restart the Sigma Server on the laptop.
Software Version Considerations
  • If using Sigma 4.05 build 3.42.34, a Hotfix is required to enable serial communications.
    👉 Download Hotfix 3.42.46
  • Later Sigma releases do not require this hotfix.
Hardware Check
  • ✅ Confirm that the RS-232 cable wiring is correct and not damaged.