Configuring a Current Input

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring a Current Input
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3431 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring a Current Input

Picard Product_Support
‎2018-09-10 11:01 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:36 AM

Issue

How to connect and configure current inputs to a UI module?

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation I/O Module 16 Ch UI (UI-16)
  • Building Operation I/O Module 8 Ch UI/4 Ch DO (Form C) (UI8-DO-FC-4)
  • Building Operation I/O Module 8 Ch UI/4 Ch AO (UI8-AO-4, UI-8/AO-V-4)
  • Building Operation MP-C, MP-V, RP-C, IP-IO

Cause

How are Current inputs connected and configured?

Resolution

To connect and configure a current input to a SmartX device no additional external resistors are required, the internal resistor in the SmartX device is automatically put into the circuit by selecting "Current Input" when creating the input object, there are no DIP switches to change as in some other products.

An external Power supply will be required to provide the current in the circuit through the sensor and into the UI input. 24V DC supplies are usually used to power the sensor & provide the current drive.

Further information regarding the SmartX device's internal resistor can be found in the Hardware Reference Guide.

Example Circuit:

The input point configuration allows you to define the top and bottom or the current scale (usually 4-20mA or 0-20mA) and the engineering units this corresponds to i.e. 0-100% or 0 - 400 DegC.

The following screen shot example shows the configuration for a 4-20mA input signal represented as 0-100%

Current Input_3864.jpg

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (6)
  • Find more articles tagged with:
  • 11747
  • analog
  • DavidChild20
  • PeterEdvik20
  • read
  • ui16
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore