Configuring Electronic Signatures for System Alarms
  • Configuring Electronic Signatures for System Alarms
  • StephenYang
    StephenYang
Admiral StephenYang Admiral
‎2024-02-07 06:51 PM
on ‎2024-02-07 06:51 PM
How can system alarms be configured so that electronic signatures are required?
Building Operation Workstation
Alarm Decoration rules are required to configure change control/electronic signatures for system alarms.
Use the Alarm Decoration filters to apply/override settings for alarms.
  1. Create an Alarm Decoration Rule under ~/System/Alarm Control Panel/Alarm Decoration
  2. Select the Alarm Decoration rule that filters on all System Alarms or the specific ones, select to override electric signature, and set it to True.
  • StephenYang24