Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Configuring Default Gateways on both Ethernet Adapters on a JACE-8000/9000

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring Default Gateways on both Ethernet Adapters on a JACE-8000/9000
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1205 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring Default Gateways on both Ethernet Adapters on a JACE-8000/9000

Guinan RandyDavis Guinan
‎2025-02-20 04:58 PM

on ‎2025-02-20 04:58 PM

Issue

Incorrect Default Gateway setting may prevent communication with the JACE-9000

Product Line

TAC IA Series

Environment

I/A Series Jace 8000/9000

Cause

The Jace8000 and Jace9000 both have primary and secondary LAN adapters. Previously, Workbench prevented users from some invalid IP configurations, but current versions of Workbench, when connecting to a 9000 will allow invalid configuration in the default gateway.

Resolution

In the 9000, a user can set different default gateways for the Primary (en0) and Secondary (en1) ports. This should not be allowed on a single network device, and leads to unpredictable behavior when routing. Compare the location of the IPv4 Default Gateway in the TCP/IP Configuration of the Platform on a 9000:

 

EN0.png

 

EN1.png

 And the same page as seen in the 8000:

EN8000.png

In future versions, this will be changed, but users should avoid invalid configurations in the affected versions.

When configuring both LAN ports for use on a 9000, only enter a value for the default gateway field in one adapter. Leave the other intentionally blank. It does not matter which is given a default gateway and which is left blank.

Note: Sometimes, when an Adapter has the Default Gateway, you cannot connect to the other Adapter (despite correctly being on that Adapter's local subnet).
These symptoms can be triggered by the Ethernet "link" (active connection) toggling up or down.  The link state can change whenever:

  • the JACE is rebooted or power-cycled; and/or
  • the Ethernet switch ("hub")  is rebooted or power-cycled; and/or
  • the Ethernet cable(s) are un- or re-plugged (at either end).

In some cases, the symptoms can alleviated by toggling the Ethernet link state, in the ways listed above.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • RandyDavis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore