Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Configure oBIX to integrate a Niagara R2 station and a Niagara G3 station

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configure oBIX to integrate a Niagara R2 station and a Niagara G3 station
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116871
    sesa116871
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3082 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure oBIX to integrate a Niagara R2 station and a Niagara G3 station

Picard Product_Support
‎2018-09-07 01:59 AM

Issue

How do I configure oBIX (Open Building Information Exchange) to integrate a Niagara R2 station and a Niagara G3 station?

Product Line

TAC IA Series

Environment

  • Niagara R2 version 5.22 and later
  • Niagara G3 version 3.4 and later

Cause

This document provides an overview of the integration of an R2 UNC to a G3 Enterprise Server using oBIX (Open Building Information Exchange).

Resolution

g3-enterprise-server-to-r2-unc.png

  1. The R2 UNC must be licensed for "obix" and the obix jar file must be in the remote library of the UNC. Add the "ObixService" to the Services container of the UNC. Re-boot the UNC.
    check-r2-unc-for-obix-service.png
  2. The G3 Enterprise Server must be licensed for obix. Double-click the Drivers Component in the G3 Enterprise Server to open the Driver Manager. Add an Obix Network.
    g3-enterprise-server-licensed-for-obix.png
  3. Double-click the new Obix Network to open the Obix Client Manager. Click the "New" button at the bottom. Add a new "R2 Obix Client."
    add-new-r2-obix-client.png
  4. Double-click the new R2 Obix Client. Enter a name for the UNC. In the Lobby field, enter http://, followed by the IP Address of the UNC, followed by "/obix". Enter the UNC's station username and password. Click OK.
    configure-new-r2-obix-client.png
    After a few seconds the state of the client should be "Attached."
    obix-client-state-attached.png
  5. Expand the UNC Device in the Nav Tree. Double-click the points component to open the Obix Point Manager. Click the "Discover" button. After the points are discovered, expand "Lobby" and then "Config." (The Lobby is the root of a Server's oBIX object tree.) You can now scroll to see the containers and objects in the UNC's station. You can add UNC points to the G3 Enterprise Server's database in the usual manner.
    obix-point-manager.png
  6. If you wish to have "link control" of objects in the UNC from the G3 Enterprise Server, then add an "Obix Export" object in the R2 Logic. These Obix Export Objects (analog, binary or multistate) are found in the Obix jar file in the remote library of the R2 UNC. Link pOut of the Export Object to pIn (if available) of the object you wish to control. Then link sOut of the R2 object back to the feedbackInput (fIn) of the export object.
    obix-export-object-in-r2-logic.png
  7. If no Priority Input is available on the R2 object, simply link the sOut of the Export Object to the sIn of the R2 object. No link to the feedbackInput of the Export Object is required.
    link-sout-of-export-object-to-sin-of-r2-object.png
  8. Return to the G3 Enterprise Server and discover the points in the R2 UNC. When adding the Export Point to the obixNetwork, the Export Objects default to type "Numeric Writable" so they can be commanded from the G2 Enterprise Server.
    g3-enterprise-server-discover-points-in-r2-unc.png
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3385
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore