Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Configure Xenta 102-AX using TGML in a Vista Classic Network (no LNS plug-in available)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configure Xenta 102-AX using TGML in a Vista Classic Network (no LNS plug-in available)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2042 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure Xenta 102-AX using TGML in a Vista Classic Network (no LNS plug-in available)

Picard Product_Support
‎2018-09-09 09:22 PM

Issue

Configuring and monitoring the Xenta 102-AX is traditionally done through the LNS Xenta 102-AX Plug-In, but how can it be done in a Vista Classic Network where no LNS plug-ins are available?

Environment

  • Vista 5 Classic Network
  • TGML
  • Xenta 102-AX
  • Vista Workstation ONLY -- This plug-in is not compatible with Webstation or XBuilder graphics at this time.

Cause

LNS Plug-ins are not available in a Vista Classic Network.

Resolution

All of the values that are written to by the LNS Plug-In are public and available through the Vista front end. So if only one or two signals need to be set for each box, this can be accomplished by locating them in the Vista network and writing the desired values to them.  This does require some fairly intimate knowledge of the Xenta 102-AX and Plug-In. The alternative is:

  1. Download the Xenta 102-AX TGML Plug-in by clicking the image below. 
  2. Unzip the contents to the hard drive.
  3. Open the TGML file.
  4. Select File > Save As > Vista Database Object
  5. Navigate to the first Xenta 102-AX in the network. Drill down into the 102-AX on the same level with Node_Object and VAV_Controller modules.
  6. Give the plug-in graphic a name and save.
  7. Right click on the Graphic object in Vista Workstation and select Copy
  8. Navigate to the next Xenta 102-AX and select Paste Shortcut. Since all bindings are automatically populated with relative bindings, copying and pasting shortcuts will automatically display data for the associated Xenta 102-AX.
  9. Repeat Step 8 for all Xenta 102-AXs in the network.

Labels (1)
Labels:
  • TAC Vista
Attachments
TGML 102AX Plugin v1.3.zip
Tags (1)
  • Find more articles tagged with:
  • 5223
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore