Configuration of automatic login into a Xenta Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuration of automatic login into a Xenta Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1700 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuration of automatic login into a Xenta Server

Picard Product_Support
‎2018-09-06 03:04 PM

Issue

Some customers may specify that the login screen to a Xenta Server be bypassed.

Environment

  • Xenta 511, 527, 555, 701, 711, 721, 731, 913

Cause

When accessing a Xenta Server using a web browser a username and password are required by default.

Resolution

  1. Configure the user you want to automatically log in to the Xenta Server
  2. Generate a certificate
    To avoid having the certificate error pop up every time you connect to the Xenta Server, go to XBuilder, and generate a certificate that has the same name as the IP address of the Xenta Server.
  3. Edit Slogin.html and loggedout.html
    1. Connect to the Xenta Server using FTP
      ftp://XXX.XXX.XXX.XXX
    2. The Slogin.html and loggedout.html are located in the folder www/index
      Copy the files to your local hard drive
    3. Edit the files with, for instance, notepad and change the following
      Slogin.html
      Line 54
      document.AuthForm.UserID.focus();"
      document.AuthForm.UserID.focus(); send(AuthForm);"

      Line 98
      input type="text" name="UserID" value="" size="20" >
      input type="text" name="UserID" value="user" size="20" >

      Line 104
      input type="password" name="PassWord" value="" size="20">
      input type="password" name="PassWord" value="password" size="20">

      loggedout.html
      Line 5 (extra line, add < symbol at beginning of line)
      meta http-equiv="refresh" content="2;url=/www/index/Slogin.html">
  4. Carry out the changes
    1. Reconnect to the Xenta Server using FTP
    2. Change the names of the files that are already in the Xenta Server (Backup)
    3. Copy the files that from your hard drive to the Xenta Server
       
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 2079
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of