Configuring a Port-Powered RS-232 to RS-485 Converter for VisiSat Communication
  • Configuring a Port-Powered RS-232 to RS-485 Converter for VisiSat Communication
  • CraigEl
    CraigEl
‎2018-09-07 08:50 AM
Last Updated: Administrator CraigEl Administrator ‎2025-10-29 09:45 PM
How do you configure VisiSat to communicate with MicroNet or IAC controllers using a port-powered RS-232 to RS-485 converter?
Field Devices, Satchwell MicroNet
  • Satchwell VisiSat
  • Any port-powered RS-232 to RS-485 converter
Proper configuration of the RS-232 to RS-485 converter is required to establish communication between VisiSat and field controllers.
Port-powered RS-232 to RS-485 converters such as the LIB-4-485 allow serial communication between a PC and RS-485-based controllers without requiring an external power supply.
Power Requirements
  • Powered directly from the PC’s RS-232 port.
  • Ensure the PC’s serial port complies with RS-232 voltage specifications.
  • Most modern PCs (e.g., Dell) are compatible, but some laptops or USB-to-serial adapters may not supply sufficient power.
Wiring Guidelines
  • TD (A) → Connect to negative (-) terminal of the controller.
  • TD (B) → Connect to positive (+) terminal of the controller.
  • GND → Connect the shield/screen only at the converter end, not at the controller.
⚠️ Always refer to the converter’s datasheet for pinout and wiring specifics.
VisiSat Server Configuration
  1. Open the VisiSat Server Client from the system tray.
  2. Go to Network Menu → Settings.
  3. In the Configure Network Settings window:
    • Set Transport Type to Serial Port
    • Click Configure
Serial Port Settings
  • Choose the appropriate configuration based on the controller type:
    • MicroNet Controllers: Use the following MicroNet-specific settings.
    • IAC Controllers: Use the following IAC-specific settings.
Click OK to apply settings. VisiSat is now ready to communicate with the controller via the RS-485 converter.
Additional Notes
  • The VisiSat Engineering Guide contains additional information regarding the VisiSat server.
  • If using a USB-to-serial adapter, ensure it supports port-powered converters.
  • For long cable runs, consider using isolated converters to prevent ground loops.