Compilation error when binding to priority array in b3 Script program
  • Compilation error when binding to priority array in b3 Script program
  • Dave_Shore
    Dave_Shore
  • Benji
    Benji
  • AbeMeran
    AbeMeran
‎2018-09-11 11:18 AM
Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2022-08-16 04:00 AM
Unable to compile a b3 Script program if there is a bind to the priority array of a commandable property.
How to command an object at a particular priority in b3 Script program.
  • b3
  • WorkStation
  • Automation Server
Because of historical reasons (that are outside the scope of this article) in the evolution of the b3 firmware, binding to the priority array of an object within a Script program in the b3 is NOT supported.
To command an object from a Script program in the b3 at a specific priority the WriteProperty command MUST be used.
NOTE If the b3 firmware is 4.500064 then priority 10 will always be set rather than the one specified in the WriteProperty command. This was fixed in v4.500076, it is best to use the the latest firmware
Tags (2)
  • 18848
  • DavidShore22
75% helpful (3/4)