Communications between a DMS-3500 and a Niagara R2 UNC-520 is slow. Points are updating very slowly.
  • Communications between a DMS-3500 and a Niagara R2 UNC-520 is slow. Points are updating very slowly.
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 01:27 PM
Communications between a DMS-3500 and a Niagara R2 UNC-520 is slow.  Points are updating very slowly.  What are some settings that can be verified and/or optimized?
Niagara R2 UNC-5x0
DMS-35, DMS-350A, DMS-3500
There could be several variables:  high count of polled objects, lower than optimal baud rate between the UNC and the DMS, non-optimal settings for the DMS Comm Service, etc....
Review the Best Practices section of the DMS Serial Driver Engineering Guide (F-27071) and apply as many of the suggestions as possible.  Among them, here are the suggestions that do not require a hardware modification or an architectural change:
  • Use the maximum allowable baud rate for the DMS serial port (38.4kb for a DMS-3500)
  • Adjust the property settings of the DmsCommService to match the following:
    • intermessageDelay = 1500
    • timeoutHostMsg = 215000
    • timeoutHostFragment = 110000
    • maxReadValues = 10
    • downDeviceRecoveryInterval = 1
    • maxMultipleMsgs = 3
    • autoCycleTimeOn = TRUE
    • deltaCycleDifference = 10
    • deltaCycleChange = 25
    • globalCycleTime = 15000
  • Ensure any DMS point alarms, that are no longer required, are programmed to not annunciate to the serial port being used to interface to the UNC.
  • Optimize polling by customizing the minimumPollInterval setting for each shadow object.  The default setting is 1000 ms.  A space temperature sensor, for example, changes very slowly.  Its setting can be modified to be anywhere from 30000 ms to 60000 ms.
  • Keep the number of Poll-Always points below 600 if they are polling at 1000 ms.