Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Communications between a DMS-3500 and a Niagara R2 UNC-520 is slow. Points are updating very slowly.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Communications between a DMS-3500 and a Niagara R2 UNC-520 is slow. Points are updating very slowly.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • Leo_Tantalo
    Leo_Tantalo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1160 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Communications between a DMS-3500 and a Niagara R2 UNC-520 is slow. Points are updating very slowly.

Picard Product_Support
‎2018-09-06 01:27 PM

Issue

Communications between a DMS-3500 and a Niagara R2 UNC-520 is slow.  Points are updating very slowly.  What are some settings that can be verified and/or optimized?

Environment

Niagara R2 UNC-5x0

DMS-35, DMS-350A, DMS-3500

Cause

There could be several variables:  high count of polled objects, lower than optimal baud rate between the UNC and the DMS, non-optimal settings for the DMS Comm Service, etc....

Resolution

Review the Best Practices section of the DMS Serial Driver Engineering Guide (F-27071) and apply as many of the suggestions as possible.  Among them, here are the suggestions that do not require a hardware modification or an architectural change:

  • Use the maximum allowable baud rate for the DMS serial port (38.4kb for a DMS-3500)
  • Adjust the property settings of the DmsCommService to match the following:
    • intermessageDelay = 1500
    • timeoutHostMsg = 215000
    • timeoutHostFragment = 110000
    • maxReadValues = 10
    • downDeviceRecoveryInterval = 1
    • maxMultipleMsgs = 3
    • autoCycleTimeOn = TRUE
    • deltaCycleDifference = 10
    • deltaCycleChange = 25
    • globalCycleTime = 15000
  • Ensure any DMS point alarms, that are no longer required, are programmed to not annunciate to the serial port being used to interface to the UNC.
  • Optimize polling by customizing the minimumPollInterval setting for each shadow object.  The default setting is 1000 ms.  A space temperature sensor, for example, changes very slowly.  Its setting can be modified to be anywhere from 30000 ms to 60000 ms.
  • Keep the number of Poll-Always points below 600 if they are polling at 1000 ms.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5886
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of