Common NetController power supply issues.
  • Common NetController power supply issues.
‎2018-09-09 09:11 PM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:00 AM
Netcontroller power supply is not working as expected.
  • NC1
  • NC2
  • CX9900
  • CX9680
  • PS120
  • UPS
Problems with Netcontroller power supply.
UPS not working
  • Replace failed 5 Amp pico fuse (located on PC board adjacent to the UPS cable connector)
  • UPS cable or connector has failed or is defective.
  • Insufficient UPS battery capacity is attached to the UPS connector.  UPS requires two 12 VDC batteries).
  • UPS Batteries are not sufficiently charged or have failed.
No Power to NetController
  • 3 Amp Slow-Blow fuse has failed.  (located on PC board adjacent to 120 volt power connector).
  • Power switch is shut off.
  • Insufficient supply voltage.
General
  • Mode switch is in the wrong position (See manual)