Commissioning HID Signo OSDP Readers Fails

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Commissioning HID Signo OSDP Readers Fails
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
264 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Commissioning HID Signo OSDP Readers Fails

Guinan AdamSteele Guinan
‎2025-10-22 12:18 AM

on ‎2025-10-22 12:18 AM

Issue

After commissioning HID Signo OSDP readers in Security Expert, they do not log card events. Readers cannot be brought online in Security Expert.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert
  • HID Signo Smart Card readers
  • HID Reader Manager App

Warning

Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Both sides of the commissioning process require proper installation steps:

  • HID Signo reader configuration using the HID Reader Manager App
  • Security Expert configuration

Resolution

Confirm Cards Work with Reader

Before starting OSDP commissioning:

  • Set the HID Signo reader to Wiegand mode.
  • Connect it to the Security Expert SP-C Reader Expander port.
  • Configure the Reader Expander and Door records for the correct format and credential.
  • Badge a card at the reader and check events in Security Expert to confirm the reader is reading the correct format.

Once confirmed, proceed to Commissioning HID Signo OSDP readers.

 

Commissioning HID Signo OSDP readers involves two main steps:

  1. Reader configuration in the HID Reader Manager App
  2. Security Expert configuration

Step 1: Configure Reader in HID App for OSDP Install Mode

  1. Open the HID Reader Manager App.
  2. Navigate to:
    Inspection Report → Detailed Configuration → Communication Protocol
    Inspect ReaderInspect Reader
  3. Enable Install Mode: 
    • Scroll down and select Add to Template.
    • Select Apply Selected Items.
      Enable OSDPEnable OSDP
  4. Wait for the reader update to complete, then exit the menus.
    Writing changesWriting changes

Step 2: Configure Reader Expander in Security Expert

  1. In Security Expert, go to:
    Reader Expander → General tab
  2. Set Port Network Type to OSDP. 
    • Saving changes creates two new Smart Reader records.
  3. Configure the Smart Reader: 
    • Set the Address correctly (1 + the address value set in the HID Reader App).
    • Under the Reader tab, set: 
      • Reader One Format to the correct format.
      • Reader One Door to the correct Door record.
  4. Activate OSDP Install Mode: 
    • Right-click the Reader Expander record → Activate OSDP Install Mode.

Expected Events

  • Install Mode Activation by <operator> on Module <module>
  • Module <module> Registered With Serial No (####)
    These indicate the command was processed and the expander attempted to register.

Important:

  • These events appear whether the OSDP handshake succeeds or fails.
  • The only way to confirm success is to badge a card and check for events.
  • OSDP Install Mode may need multiple attempts for successful handshaking.
  • When successful, the HID Reader Manager App will automatically disable Install Mode, which can be confirmed in the App.

Key Notes

  • Always verify card functionality before starting OSDP commissioning.
  • Multiple attempts may be required for OSDP handshake.
  • Successful commissioning is confirmed by card events in Security Expert.

 

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • AdamSteele25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore