Clear the memory of an MR
  • Clear the memory of an MR
‎2018-09-07 12:22 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:36 AM
How can I clear the memory of an MR?
MR
If an MR with a database is given a new address using the dip switches, the DDC, I/STAT parameters and points remain in its memory.
The only way truly clear the memory is to use an I/STAT or M/STAT:
  1. Enter the service mode
  2. Re-enter the address or communication speed.
  3. Changing these parameters can work but be careful not to leave the speed at anything other than 9600.
Refer to the I/STAT instructions in TCON 126 or TCON 130 for instructions on service mode operations.
  • TAC INET
  • 1619
100% helpful (1/1)