Changing the link number associated with the I/NET interface in the AS level integration to I/NET
  • Changing the link number associated with the I/NET interface in the AS level integration to I/NET
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 08:43 AM
Multiple issues caused by changing the link after discovering devices.
  • Duplicate entries of MCU devices under a sub LAN interface
  • Deleting duplicate MCUs causes MCU devices to be removed from I/NET
Automation Server integrated to I/NET
Changing the link address of the I/NET Interface should not be done after devices are discovered. If you must change the link address, do so before you have added devices to the I/NET interface.
Option 1 -
  1. Remove all controllers from the I/NET interface.
  2. Change the link to the correct setting
  3. Re-discover the devices
Option 2 -
  1. Determine whether the AS or the I/NET controller has the correct information. (This will require I/NET software)
  2. If the AS is more correct, perform a download to the controller
  3. if the I/NET controller is more correct, perform an upload to the AS
Labels (2)
  • TAC INET
  • 18272