Changes to COV and Point to point polling in Continuum BACnet Controllers as of Version 4.5 drop 48 and above

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Changes to COV and Point to point polling in Continuum BACnet Controllers as of Version 4.5 drop 48 and above
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • Product_Support
    Product_Support
  • sesa101527
    sesa101527

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1622 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Changes to COV and Point to point polling in Continuum BACnet Controllers as of Version 4.5 drop 48 and above

Picard Product_Support
‎2018-09-06 02:33 PM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2022-09-08 07:33 AM

Issue

Changes to COV and ReadProperty in bCX from v4.500048

Product Line

Andover Continuum

Environment

  • bCX
  • b3 Controllers

Cause

New feature to allow user flexibility for using Forced Polling and not COV

Resolution

From bCX version v4.500048, all Controllers will have the option of forcing a poll of points from other Continuum and third party BACnet controllers.
This new feature:

  • allows programmers to decide which data exchange method to use by the syntax in which they write their data-sharing programs.
  • provides a method for forcing point-to-point polling from a device that does not support COV and sends an invalid error message when the subscription is attempted. This previously caused Continuum to reject polling, resulting in a failure to share data.
  • allows programmers to decide to poll a point only when needed, even if the device supports COV subscriptions. This ensures that data from a device is only sent when necessary instead of always being sent on a “change of value”.


The following Plain English formats force polling:
"Local point = Infinity Remote Point Value"
"Local point = BACnet Remote point Value"
"Local point = ReadProperty(BACnet Remote point Value)"


The second argument, Value, ensures that polling is commanded – now for BACnet, as well as Continuum/Infinity.
(The third example shows the use of Plain English’s ReadProperty system function.) If the Value argument, shown in these examples, is left out, Continuum BACnet will operate as it always has – always attempting a COV subscription and only falling back to the polling method if the target device sends the appropriate COV subscription failure message.

Caution:
If you have a device that does not support COV subscriptions or you have chosen to use the polling syntax, you must be careful how you write your Plain English programs. A program that runs every scan and polls a point from another controller will cause major problems.
For instance, if your scan is running at 100 milliseconds and you try to poll any BACnet device at that rate, you will most likely knock the device offline. It will also cause the program to disable and seriously slow down the scan in your controller that is requesting the data (since the scanner waits for an answer to a poll before continuing).
You should also use a line E in your programs, since any communication problem to the target device will cause the polling program to disable.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 3641
  • DavidShore22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of