Change routers from repeaters to configured to decrease network traffic
  • Change routers from repeaters to configured to decrease network traffic
‎2018-09-06 03:29 PM
Routers / i.Lons configured as repeaters pass everything and consume bandwidth causing throughput / slowness issues in your system.
  • LON physical layer
  • L-IP routers
The cause of throughput/slowness issues in a network might be that it is bogged down with needless communication.
  1. Configure router ports as "Repeater" to avoid channel conflicts during the construction phase of a project.
  2. After all of the nodes are commissioned, configure all routers as configured routers so that they only pass what is necessary upstream.
  3. This is especially important if using i.Lon 1000s, 600s, or Loytec L-IP routers as they will pass that unneeded data onto the ethernet.