Issue
New use for nviAirFlowReset in Heat mode on an Xenta 102-AX - change the flow setpoint based on heating demand.
Product Line
TAC Vista
Environment
Xenta 102-AX 2.12 and later
Cause
Xenta 102-AX 2.12 introduced some new features with heating flow control. Before it would only provide the Heating Low Flow setpoint any time the unit was in heat mode. With 2.12, the warmup max was introduced which allows reset of flow setpoints between these two values in heat mode. The nviAirFlowReset signal allows for altering the effective flow setpoint based on a looped back output of the heating demand.