Central I/O Input and Output Specifications
  • Central I/O Input and Output Specifications
‎2018-09-11 01:25 PM
Last Updated: Crewman ContentModerator ‎2025-10-15 03:40 AM
Questions regarding specifications of Central I/O Inputs and Outputs
SmartStruxure I/O Modules:
  • AO-8, AO-8-H
  • AO-V-8, AO-V-8-H
  • DI-16
  • DO-FA-12, DO-FA-12-H
  • DO-FC-8, DO-FC-8-H
  • RTD-DI-16
  • UI-8-AO-4, UI-8-AO-4-H, UI-8/AO-4-2, UI-8/AO-4-H-2
  • UI-8-AO-V-4, UI-8-AO-V-4-H, I/O UI-8/AO-V-4-2, UI-8/AO-V-4-H-2
  • UI-8-DO-FC-4, UI-8-DO-FC-4-H, UI-8/DO-FC-4-2, UI-8/DO-FC-4-H-2
  • UI-16
Different I/O modules have varying electrical specifications
Universal Input Specifications
Universal inputs can be configured as voltage, current, thermistor, resistance, digital or supervised inputs.
Voltage Input Specifications:
  • Range: 0 to 10 VDC
  • Resolution: 12-bit (UI-8 v2: 16-bit)
  • Accuracy: ±(0.7mV + 0.2% of reading)
Current Input Specifications:
  • Range: 0 to 20 mA
  • Accuracy: ±(0.03 mA + 0.4% of reading)
Resistance Input Specifications:
  • 10 Ohm to 10 kOhm
  • 10 kOhm to 60 kOhm
Thermistor Input Specifications:
  • Range: -50 to 150° C (-58 to 302° F)
  • Supported Types:
    • 10k Type I (Continuum)
    • 10k Type II (I/NET)
    • 10k Type III (Satchwell)
    • 10k Type IV (FD)
    • 1.8k (Xenta)
    • 10k Linearized (Satchwell DRT)
    • 10k Type V (FD w/ 11k shunt)
    • 1k (Balco)
    • 20k (Honeywell)
    • 2.2k (Johnson Controls)
Digital Output Specifications
Form C Relay:
  • Terminals: Common (C), Normally Open (NO), Normally Closed (NC)
  • Minimum Pulse Width: 100 ms
  • Isolation: 1500 VAC (coil to contact)
  • Cycle Life: ≥100,000 cycles
  • Contact Rating: 250 VAC, 30 VDC, 3 A
Form A Relay:
  • Contact Rating: 250 VAC, 30 VDC, 2 A
LED Indicators:
  • Polarity: Reflects actual output state (ON = active, OFF = inactive)
  • Color: Green
Analog Output Specifications
Analog outputs can be configured as voltage or current.
Voltage Output:
  • Resolution: 50 mV
  • Accuracy: ±100 mV
  • Terminals: Voltage (V), Return
  • Minimum Load: Source 2 mA, Sink -1 mA
Current Output:
  • Range: 0 to 20 mA
  • Resolution: 0.1 mA
  • Accuracy: ±0.2 mA
  • Terminals: Current (I), Return
  • Max Load: ≤650 Ohms
Supervised Input Specifications
Supervised inputs detect sabotage via resistor monitoring.
  • Detected Conditions: Open circuit, short circuit, contact open/closed
  • Circuit: 5V, 1 or 2 resistors
  • Configurations: Series only, parallel only, series + switch
  • Resistor Range: 1k to 10k Ohms (must be equal values)
  • Note: Resistor value must be defined in the system.
RTD Input Specifications
RTD-DI-16 specifications are extensive.
Refer to the official datasheet: RTD-DI-16 Specification Sheet
Tags (2)
  • 17333
  • CraigEllis25
100% helpful (3/3)