Cannot open history in a G3 station, get error "java.lang.IllegalArgumentException: duplicate name history".
  • Cannot open history in a G3 station, get error "java.lang.IllegalArgumentException: duplicate name history".
  • SESA113595
    SESA113595
‎2018-09-06 10:24 AM
Cannot open history in the station, error  as follows:
ERROR [13:02:33 25-Apr-13 PDT][sys.service] Service start failed: History Service
   at javax.baja.nav.BNavContainer.addNavChild(BNavContainer.java)
   at javax.baja.naming.BHost.addNavChild(BHost.java)
   at javax.baja.history.BHistoryService.initDataRecoverySource(BHistoryService.java)
I/A Series G3 station
Duplicate name of history.
Using Workbench:
  1. Connect to the station and go to the property sheet view of the root config of the station.
  2. Hit ctrl + L, which opens the current ord dialog
  3. Paste in the below text to the end of the current ord.
    |bql:select slotPath,name from history:HistoryService
  4. It should display a table and show the slot path of each of the history service components.
  5. Locate and delete the extra service.
  • TAC IA Series
  • 13216