Cannot learn in B3 controllers
  • Cannot learn in B3 controllers
‎2018-09-10 12:48 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:35 AM
Trying to add B3 controllers to BCX and they are not coming online.
Andover Continuum
  • BCX 4040
  • Continuum 1.9X
  • B3XXX  controllers
BacNet wiring can not be in a star configuration. There can not be more than two terminating 120 Ohm resistors.
  1. The Bus must be wired in series with end line 120 Ohm resistors.
  2. Install a B-Link if the bus path cannot be wired in series.
Please see the BacNet Technical Reference manual for wiring examples.