Cannot configure BACnet MSTP port after first enabling it.
  • Cannot configure BACnet MSTP port after first enabling it.
  • sesa116868
    sesa116868
‎2018-09-06 01:28 PM
Updated license to add additional BACnet MSTP ports on the ENC and rebooted. After rebooting the added MSTP port could be enabled but the port settings could not be changed.
UNC 520
UNC license file shows "numberOfBACnetMSTPTrunks=2" (or 3 or 4)
Failure to reboot the UNC after enabling the BACnet MSTP port in the UNC
Reboot the UNC after enabling the BACnet MSTP port.
The UNC's BACnet service will automatically detect any saved BACnet port configuration changes and will apply the changes immediately.
  • TAC IA Series
  • 5828